The problem with using a charger that can solar divert independent of a solar/battery setup is that there will be are 2 CT clamps on the grid side of the meter box - 1 to charger, the other to inverter/energy controller of battery. R. Which one takes priority? Or maybe both do not know the other is there.
Example: excess solar and system starts to export 5kW. The CT clamp to charger and CT clamp to house battery detects that excess. Both would use 5kW by itself. What happens if both turn on at the same time. Both would then detect zero export then turn off. Rinse and repeat.
I suggest having a EV charging solar divert system that is integrated with the gateway of the Solar/battery or at least can communicate with the solar/battery inverter
Alternatively use a 3rd party app like ChargeHQ which communicates with the charger EV and the solar/battery via their respective API to control solar diversion.
Good points to consider if and when we install home battery. We don’t have one at present and based on current and projected power usage the payback period is >10years and not sure I want to invest.
Trying to juggle the balls in my head on competing priorities of not over capitalising, minimising energy expenditure, the evolution of technology (we are on the cusp of a few things such as V2H, battery technology etc), limited time government subsidies, mitigating impacts of power outages and others.
Edit: googleAI has suggested a method to avoid the stalemate of 2xCT clamps by prioritising the clamps and settings to prevent the home battery supplying the car. It has suggested amended wording for electrician quote request in preparation for future home battery installation and avoid rework.